120-3-3-.04(121)(a)(1) indicates NFPA 291 (2002) provides 
recommendations for flow testing. Due to the importance of accurately predicting 
the water supply available for fire protection, pressure gauges used for the 
waterflow test necessitate having their calibration tested within the last 
twelve months in accordance with NFPA 291 (1998), Section 4.4.2, and the test 
should be witnessed by the Local Fire Official or Water Department. Submit a 
copy of calibration tests indicating test gauges comply with ASME standards and 
therefore the waterflow test complies with this section. The waterflow test date 
must comply with 120-3-3.04(6)(e), Part 1, modifications to NFPA 13 (2002), 
which added Section 15.2.1.3, requires water flow test to be performed within 
six months of plan submittal, and the test was duly witnessed by the local Fire 
Department per 2003 IFC, Section 508.4. Finally, the Hydraulic Calculations must 
comply with 120-3-3.04(6)(d), Part 2, modifications to NFPA 13 (2002), which 
added Section 14.4.4.8.3, requiring a minimum 10 psi cushion safety 
factor.