by Blackstone
on Fri Nov 21, 2008 3:27 pm
120-3-3-.04(121)(a)(1) indicates NFPA 291 (2002) provides
recommendations for flow testing. Due to the importance of accurately predicting
the water supply available for fire protection, pressure gauges used for the
waterflow test necessitate having their calibration tested within the last
twelve months in accordance with NFPA 291 (1998), Section 4.4.2, and the test
should be witnessed by the Local Fire Official or Water Department. Submit a
copy of calibration tests indicating test gauges comply with ASME standards and
therefore the waterflow test complies with this section. The waterflow test date
must comply with 120-3-3.04(6)(e), Part 1, modifications to NFPA 13 (2002),
which added Section 15.2.1.3, requires water flow test to be performed within
six months of plan submittal, and the test was duly witnessed by the local Fire
Department per 2003 IFC, Section 508.4. Finally, the Hydraulic Calculations must
comply with 120-3-3.04(6)(d), Part 2, modifications to NFPA 13 (2002), which
added Section 14.4.4.8.3, requiring a minimum 10 psi cushion safety
factor.
We find consulations, we learn tricks with which
we deceive ourselves, but the essential thing - the way - we do not find. Listen
to the river.
JBlackstone@GAInspector.Org