Had an engineer for a Wal-Mart project (wanting to use a 
preaction system outside in their garden center to avoid the higher water demand 
of a dry system) run the Fire Dynamics Simulator (FDS) fire model on a few 
scenarios with differing RTI’s with a small cross wind as the worst case 
scenario and 
they could not prove even to themselves 
(much less myself who questioned the use of a preaction system 
outside where the detection system would be essentially useless thus relying on 
a sprinkler to activate on dry pipe...) that the heat detectors (we eliminated 
smoke detectors for obvious reasons - remember this is outside with winds...) 
would open the valve in enough time to warrant eliminating the system acting 
like a dry system.
They were allowed a preaction outdoors, but not 
without the 30% increase as was justified in the model I made them check into 
for verification. They kept the detection system for their own reasons, it just 
was not recognized as a preaction system – just a dry system with fire 
detection. Would probably be prudent for NFPA to consider putting some kind of 
limitation on the use of preaction outdoors as I had done (i.e. outdoor 
preaction system design area of operation shall be hydraulically calculated as a 
dry system)… or at the very least investigate this issue ~ heck, even 120-3-3 
should at least have such an amendment 