by Blackstone
on Fri Nov 21, 2008 2:27 pm
The standpipe requirement comes from the 2006 IFC, Section
905, which allows sprinklered buildings to use a Class I standpipe which may be
a manual wet standpipe unless it is a high-rise which requires it to be
automatic per NFPA 14 (2003), Section 5.4.1.2. A manual wet standpipe still
requires compliance with NFPA 14 (2003), Section 7.7.1 (new section in the 2003
edition) which must be calculated thru the FDC to the pumper thus avoiding a
fire pump (at least for standpipe demand). Non-sprinklered buildings require a
Class III which NFPA 14 requires to be automatic, not manual per NFPA 14 (2003),
Section 5.4.3, and which could still require a fire pump but again this is in a
building that is not incurring the cost of a sprinkler system so cost are offset
a bit. 100 psi has been found to be what is needed to fight a fire using 1½“
hose streams, which can be provided by the pumper truck in non-high-rise
buildings avoiding a fire pump, and we really don’t need to be reducing the fire
fighter’s resources by allowing a 65 psi except for hardship cases.