All backroom emergency exit access
paths (e.g. from sales areas thru stockrooms) shall be provided with floor
markings and protective handrails to prevent storage/equipment from blocking the
means of egress where the exit access passes thru these areas in accordance with
the 2000 LSC, Section 36.2.5.10(4) requirements. Plans must indicate any exit
access isles (stock/receiving or sales area), method of ensuring aisles are kept
clear, etc. Include exit access information on plans.
Provide sprinkler
protection below any front canopy as required by NFPA 13 (2002), Section
8.14.7.4, as this area is typically used by merchants for the display of
merchandise for seasonal sidewalk sales (e.g. holiday merchandise, overstock
sales, sidewalk sales, etc.). Include protection below any loading dock
canopy.
Since no areas of any storage rooms have been indicated with high
piled storage (Class I thru IV combustible storage exceeding 12-ft in height);
then conspicuous signage shall be provided throughout any storage room
indicating “Maximum Storage 12-ft by Order of Fire Marshal”.
High hazard
commodities stored over 6-ft high such as appreciable quantities of Group A
Plastics, rubber tires, flammable/combustible liquids, aerosols, oxidizers,
etc., or any storage over 12-ft high of Class I thru IV commodities, shall be
required to comply with 2003 IFC, Chapter 23 requirements. Section 2301.3
requires plans submitted for building permit include all information identified
in this section including all proposed fire protection requirements, design
features, etc., required by Item 14 of this section. Include a Hazardous
Materials Storage Summary (Haz-Mat Disclosure) indicating all physical
(oxidizers, flammable/combustible liquids, aerosols, etc.) and health (toxic,
corrosive, etc.) hazards to be stored in the facility as required by 2003 IFC,
Section 2701.5.2. Submittal shall include: key plan indicating locations of
items in disclosure; list of materials indicating type and quantities (product
grouping and general hazard info), container size, and maximum storage size
(area and height). MSDS and emergency procedure information are not required to
be included in this submittal, but shall be made available to the Fire Marshal
prior to issuance of the facility's Certificat of Occupancy.