Since 2003 IFC, Section 903.3.1.2.1, specifically addresses 
residential occupancies of Type V 
construction and the Life Safety Code nor NFPA 13R does not, then as a 
supplemental code, it is applicable that balconies and patios “of the dwelling 
units” (this would not apply to balconies and patios for the entire building) 
would be required to be sprinklered even for a 13R sprinklered residential 
occupancy building,.
The ‘dwelling unit’ is the single housekeeping unit 
consisting of living room, bedroom(s), toilet, private balcony/patio/deck, 
closets, kitchen, etc. used by a single tenant/family. Egress balconies, 
porches, etc. used for common egress are ‘outside the dwelling unit’ by 
definition (see NFPA 13R), and therefore this specific code section does not 
apply to them.
The 2003 IFC commentary indicates the reason for this 
section is because of typical grilling, Bar-B-Q’s, tiki lamps, etc., that are 
frequently placed on residential patios/balconies that are a fire hazard. 
Patios/balconies off of the dwelling unit front door, used as a common area for 
exit access (more of an exterior walkway than a true balcony) by all the 
tenants, typically do not contain these activities (or at least these hazardous, 
open flame activities are forbidden in a means of egress…), would be exempt from 
sprinkler requirements in a 13R system.
This section combined with the 
open flame requirements of 2003 IFC, Section 308.3.1 (restricting these grills, 
etc. to be loacted within 10-ft of combustibles), help to protect the building 
from a fire that would grow much too large for the 13R system to handle.