Smoke Control 
System Shop Drawing Submittals
The following 
information is provided as a guide to assist those submitting Smoke Control 
System Shop Drawings for Review and Approval:
1. 2003 IFC, Sections 
909.10 and 909.4.4 requires the exhaust system (fan, motor, etc.) to consider 
the effects of the fire on the system. The exhaust fan must be rated to 
withstand the predicted maximum temperature that the system could experience, 
and where the fire could be located directly below the unit, the temperature 
must be evaluated and a means provided to ensure the fire shall not adversely 
affect the unit(s) (e.g. 3000ºF rated unit). Ensure exhaust fans are UL Listed 
(ZAXH) for Smoke Control Systems ~ all detection and control components are 
required to be UL Listed (UUKL or UUKL2) for Smoke Control Systems (UL 864) per 
2003 IFC, Section 909.12.
2. Automatic exhaust louvers (natural supply) 
in combination with automatically operated doors (mechanical supply) are 
acceptable make-up air sources. Indicate the mounting height of all makeup air 
device(s) and provide data sheets on the natural and mechanical system equipment 
for review.
3. Provide a detailed layout (1/4 scale or larger) of the 
Fire Command Center for review and approval per 2003 IFC, Section 509.1 
requirements. Layout shall indicate all applicable components listed in items 1 
thru 15 of this section, complete with make, model, etc. Ensure equipment layout 
has been coordinated with local Fire Official prior to submitting to this office 
for review and approval. The Fire Command Center and Generator Rooms must be a 
minimum of a 1-hour Fire Barrier per 2003 IFC, Sections 509.1 and 
909.11.
4. 2003 IFC, Section 909.18.8.2 requires those performing the 
Smoke Control System Acceptance Test to have expertise in: Fire Protection 
Engineering; Mechanical Engineering; and Certification as Air Balancers. Special 
inspections are required per Section 909.18.8.1 such as during construction and 
near completion before the acceptance test.
5. All wiring for the Smoke 
Control System (including wiring from FACP to Smoke Control Panel) shall be 
enclosed in continuous raceways per 2003 IFC, Section 909.12.1. Fire Alarm 
System wiring shall comply with 2002 NAC Article 760 requirements.
6. 
Smoke Control exhaust fans used for dual purposes shall ensure the Smoke Control 
function will override any auxiliary uses (such as warm weather ventilation) 
during emergency conditions.
7. The Smoke Control System Design should 
include addressing axisymmetric fire plumes, and as applicable, window or 
balcony spill plumes and plumes in contact with walls. Atriums of unconventional 
design (long and narrow, multiple levels with relatively small opening to floor 
ratios, unique geometric configurations, etc.) should use the NFPA 92B and 2003 
IFC empirical formulas only as a starting point for preliminary calculations 
for estimation (see more info at: http://go.rwdi.com/technotes/t13.pdf 
), and then use a Computational Fluid Dynamic (CFD) Fire Models (e.g. Fire 
Dynamic Simulator ~ FDS) used for the actual final design layout, fan sizing, 
etc.
8. Section 909.11 requires a secondary power supply (to fans, 
make-up air devices, etc.). Provide information indicating compliance with this 
section.
9. Section 909.12 indicates detection and control system 
requirements. Provide information (diagram, matrix, etc.) on interface to Fire 
Alarm System, Smoke Control Panel, etc., and include layout of detection 
devices, and layout of exhaust/makeup air equipment.
10. 2003 
International Fire Code (IFC), Section 909.16 requires a Smoke Control Panel 
complying with Sections 909.16.1 through 909.16.3 to be located in a Fire 
Command Center complying with 2003 IFC, Section 509.
11. All submitted 
drawings shall be on an unalterable medium (i.e. no vellum, mylar, pencil, 
adhesive applied details, etc.). Include a Transmittal Form with all submittals, 
in addition to two full sets of Smoke Control System Shop Drawings, a copy of 
the approved sealed engineering analysis (drawings, calculations, etc.) complete 
with a copy of its comment sheet, and two copies of any data sheets (fans, 
controls, 
etc.).
________________________________________________________________
Smoke Control 
Design Considerations
The belief that NFPA 92B, 
Section 2.4.2.3.1 saying that the balcony spill plume formula is only valid for 
non-sprinklered spaces and should not be used is not quite what this section is 
trying to get across! The section is indicating the formula is derived from 
non-sprinklered spaces true enough (even 1/10th scale experiments!), however 
since it’s accuracy was based on non-sprinklered spaces, when used in 
sprinklered spaces, the dynamics of the sprinklers should be taken into 
consideration in some cases – this in addition to the geometry involved 
(location of fire, lintels, draft-stops, etc.).
Worst case is the 
sprinkler system has a valve shut, MIC has reduced the pipe cross section to 
effectively nothing, etc., and the smoke control is not affected by sprinklers 
(a CFD fire model such as the Fire Dynamics Simulator will also show that even 
in an unsprinklered space, the geometry itself can cause bizarre curling 
vortexes ~ see http://go.rwdi.com/technotes/t13.pdf 
for more about how these NFPA 92B formulas are supposed to be only a starting 
place, and in situations involving complex atria, fire modeling should be the 
next step).
Conversely, the sprinklers work and you get bizarre curling 
vortexes which impinge on different levels, etc. due to the interaction with the 
water droplets, cooling, etc. - or perhaps even a smaller fire due to 
suppression system controlling the fire which the smoke control system will 
easily deal with.
The ICC people in the 2006 version appear to have just 
ducked-out of the controversy by removing the formula’s all together and 
defaulting to whatever NFPA 92B says – they have not said balcony spill 
calculations are not required for sprinklered spaces. The 2004 supplement to the 
2003 IFC had originally just removed the requirement, but with all the 
controversy of the balcony spill formula the next edition just removed ALL the 
formulas (axisymmetric, window, etc.) and just left it up to NFPA…
As far 
as valid reasons not to require a balcony spill calculation - a fairly narrow 
balcony that would not appreciably affect the plume (such as a running track 
around the top of a gym, etc.) would be one such case for omitting the 
calculations, just as omitting the window spill calculations if all openings are 
few and relatively small, etc. Sure, not all the formulas are always relevant 
since atriums differ – some have no windows or balconies.
Perhaps the 
balcony spill plume calculations are a bit overly conservative, but until the 
ASHRAE/IRC research is done, it is better than just ignoring the phenomena. If 
the balcony spill plume calculations are indicating a smoke production rate that 
seems exorbitant, one could try using CFD fire modeling as an alternative which 
would be the more prudent approach than just saying the calculations are not 
required at all.
The smoke development analysis in each of the design 
approaches must be justified using algebraic calculations for preliminary 
calculations only, unless approved by the Authority Having Jurisdiction for 
atria with simple geometry’s and a single floor openings (to limit use of 
equations outside their validation), and detailed design calculations using (to 
require modeling for other than very simple atria) zone, scale, computational 
fluid dynamics (CFD), and compartment fire models. Computational fluid dynamics 
(CFD) models must be used for atria 
designs with complex geometry and/or multiple floor openings when required by 
the Authority Having Jurisdiction (to permit AHJ to judge complexity of atria 
and require a state of the art simulation type model).