Smoke Control
System Shop Drawing Submittals
The following
information is provided as a guide to assist those submitting Smoke Control
System Shop Drawings for Review and Approval:
1. 2003 IFC, Sections
909.10 and 909.4.4 requires the exhaust system (fan, motor, etc.) to consider
the effects of the fire on the system. The exhaust fan must be rated to
withstand the predicted maximum temperature that the system could experience,
and where the fire could be located directly below the unit, the temperature
must be evaluated and a means provided to ensure the fire shall not adversely
affect the unit(s) (e.g. 3000ºF rated unit). Ensure exhaust fans are UL Listed
(ZAXH) for Smoke Control Systems ~ all detection and control components are
required to be UL Listed (UUKL or UUKL2) for Smoke Control Systems (UL 864) per
2003 IFC, Section 909.12.
2. Automatic exhaust louvers (natural supply)
in combination with automatically operated doors (mechanical supply) are
acceptable make-up air sources. Indicate the mounting height of all makeup air
device(s) and provide data sheets on the natural and mechanical system equipment
for review.
3. Provide a detailed layout (1/4 scale or larger) of the
Fire Command Center for review and approval per 2003 IFC, Section 509.1
requirements. Layout shall indicate all applicable components listed in items 1
thru 15 of this section, complete with make, model, etc. Ensure equipment layout
has been coordinated with local Fire Official prior to submitting to this office
for review and approval. The Fire Command Center and Generator Rooms must be a
minimum of a 1-hour Fire Barrier per 2003 IFC, Sections 509.1 and
909.11.
4. 2003 IFC, Section 909.18.8.2 requires those performing the
Smoke Control System Acceptance Test to have expertise in: Fire Protection
Engineering; Mechanical Engineering; and Certification as Air Balancers. Special
inspections are required per Section 909.18.8.1 such as during construction and
near completion before the acceptance test.
5. All wiring for the Smoke
Control System (including wiring from FACP to Smoke Control Panel) shall be
enclosed in continuous raceways per 2003 IFC, Section 909.12.1. Fire Alarm
System wiring shall comply with 2002 NAC Article 760 requirements.
6.
Smoke Control exhaust fans used for dual purposes shall ensure the Smoke Control
function will override any auxiliary uses (such as warm weather ventilation)
during emergency conditions.
7. The Smoke Control System Design should
include addressing axisymmetric fire plumes, and as applicable, window or
balcony spill plumes and plumes in contact with walls. Atriums of unconventional
design (long and narrow, multiple levels with relatively small opening to floor
ratios, unique geometric configurations, etc.) should use the NFPA 92B and 2003
IFC empirical formulas only as a starting point for preliminary calculations
for estimation (see more info at: http://go.rwdi.com/technotes/t13.pdf
), and then use a Computational Fluid Dynamic (CFD) Fire Models (e.g. Fire
Dynamic Simulator ~ FDS) used for the actual final design layout, fan sizing,
etc.
8. Section 909.11 requires a secondary power supply (to fans,
make-up air devices, etc.). Provide information indicating compliance with this
section.
9. Section 909.12 indicates detection and control system
requirements. Provide information (diagram, matrix, etc.) on interface to Fire
Alarm System, Smoke Control Panel, etc., and include layout of detection
devices, and layout of exhaust/makeup air equipment.
10. 2003
International Fire Code (IFC), Section 909.16 requires a Smoke Control Panel
complying with Sections 909.16.1 through 909.16.3 to be located in a Fire
Command Center complying with 2003 IFC, Section 509.
11. All submitted
drawings shall be on an unalterable medium (i.e. no vellum, mylar, pencil,
adhesive applied details, etc.). Include a Transmittal Form with all submittals,
in addition to two full sets of Smoke Control System Shop Drawings, a copy of
the approved sealed engineering analysis (drawings, calculations, etc.) complete
with a copy of its comment sheet, and two copies of any data sheets (fans,
controls,
etc.).
________________________________________________________________
Smoke Control
Design Considerations
The belief that NFPA 92B,
Section 2.4.2.3.1 saying that the balcony spill plume formula is only valid for
non-sprinklered spaces and should not be used is not quite what this section is
trying to get across! The section is indicating the formula is derived from
non-sprinklered spaces true enough (even 1/10th scale experiments!), however
since it’s accuracy was based on non-sprinklered spaces, when used in
sprinklered spaces, the dynamics of the sprinklers should be taken into
consideration in some cases – this in addition to the geometry involved
(location of fire, lintels, draft-stops, etc.).
Worst case is the
sprinkler system has a valve shut, MIC has reduced the pipe cross section to
effectively nothing, etc., and the smoke control is not affected by sprinklers
(a CFD fire model such as the Fire Dynamics Simulator will also show that even
in an unsprinklered space, the geometry itself can cause bizarre curling
vortexes ~ see http://go.rwdi.com/technotes/t13.pdf
for more about how these NFPA 92B formulas are supposed to be only a starting
place, and in situations involving complex atria, fire modeling should be the
next step).
Conversely, the sprinklers work and you get bizarre curling
vortexes which impinge on different levels, etc. due to the interaction with the
water droplets, cooling, etc. - or perhaps even a smaller fire due to
suppression system controlling the fire which the smoke control system will
easily deal with.
The ICC people in the 2006 version appear to have just
ducked-out of the controversy by removing the formula’s all together and
defaulting to whatever NFPA 92B says – they have not said balcony spill
calculations are not required for sprinklered spaces. The 2004 supplement to the
2003 IFC had originally just removed the requirement, but with all the
controversy of the balcony spill formula the next edition just removed ALL the
formulas (axisymmetric, window, etc.) and just left it up to NFPA…
As far
as valid reasons not to require a balcony spill calculation - a fairly narrow
balcony that would not appreciably affect the plume (such as a running track
around the top of a gym, etc.) would be one such case for omitting the
calculations, just as omitting the window spill calculations if all openings are
few and relatively small, etc. Sure, not all the formulas are always relevant
since atriums differ – some have no windows or balconies.
Perhaps the
balcony spill plume calculations are a bit overly conservative, but until the
ASHRAE/IRC research is done, it is better than just ignoring the phenomena. If
the balcony spill plume calculations are indicating a smoke production rate that
seems exorbitant, one could try using CFD fire modeling as an alternative which
would be the more prudent approach than just saying the calculations are not
required at all.
The smoke development analysis in each of the design
approaches must be justified using algebraic calculations for preliminary
calculations only, unless approved by the Authority Having Jurisdiction for
atria with simple geometry’s and a single floor openings (to limit use of
equations outside their validation), and detailed design calculations using (to
require modeling for other than very simple atria) zone, scale, computational
fluid dynamics (CFD), and compartment fire models. Computational fluid dynamics
(CFD) models must be used for atria
designs with complex geometry and/or multiple floor openings when required by
the Authority Having Jurisdiction (to permit AHJ to judge complexity of atria
and require a state of the art simulation type model).