by Blackstone
on Fri Nov 21, 2008 3:23 pm
Hydraulic Calculations for each hydraulically calculated area
on all submittals shall be a single set of calculations made from the remote
area to the point of the waterflow test per NFPA 13 (2002), Section 14.4.4, not
to an estimated/separately-calculated available supply at the riser, pump
discharge, or other obscure location (calculations shall start with the flow and
pressure demand at the most hydraulically demanding single point in the system,
and work back to the point where the water supply test was performed adding all
pressure losses [friction, elevation, etc.] and additional flows [hose, in-rack,
etc.] to determine the total water demand at the available water supply
validating such demand). (Note: As this cushion is required for the finish
installation, an additional safety factor may be prudent to compensate for any
changes to the design from field conditions, any addenda, etc.)
We find consulations, we learn tricks with which
we deceive ourselves, but the essential thing - the way - we do not find. Listen
to the river.
JBlackstone@GAInspector.Org