A Main Drain Test Connection shall be provided for each 
sprinkler riser per NFPA 13 (2002), Section 8.16.4.1.1, and sized per NFPA 13 
(2002), Table 8.15.2.4.2 ~ main drain piping size is based upon:
 
Providing sufficient flow to properly determine the valve is fully open (the 
basis of the main drain minimum size);
 Provide a point on the riser to 
perform main drain waterflow testing (not specifically addressed in NFPA 13 [a 
minimum standard], but frequently used by inspectors, insurance representatives, 
engineers, investigators, etc. ~ see IRI’s IM.14.1.2.2 data sheet for more 
information on main drain waterflow tests and its appropriateness); 
and,
 Provide efficient draining of the system (note: inspector’s test 
piping is used for waterflow device testing, not waterflow testing).
Any 
common drain pipe (gang drain / drain riser) serving multiple main drain 
connections needs to be one pipe size larger than the largest main drain tied 
into it (Note: NFPA 13 (2002), Section 8.15.2.4.7 requires increasing the common 
drain piping for floor control valves for similar reasons) so that main drain 
flow (valve) and waterflow (supply) tests may be successfully performed on the 
risers when needed. An alternative would be to provide separate main drain 
discharge piping for each riser.

