OK, some times you’ll see a dry insp. test conn. on a dry
system that is essentially a drum drip with an orifice in the discharge elbow –
this is an attempt to ‘combine’ these two devices (drum drip as a low point
condensation drain, and the dry insp. test conn.). This is acceptable, but the
removable segment with plug/nipple and cap is frequently left out in an act of
sheer stupidity. Below is the correction comment for this issue:
The dry
pipe test connection may include a drum drip [condensation drain], however the
lower valve shall be sealed with a plug [or nipple and cap] to avoid leakage of
air which could accidentally trip dry pipe valve and cause nuisance alarms ~
these valves are designed for a wet valve seat, and over time, air will seep
thru the dry rubber valve seat ~ a removable pipe section [union, groove
fitting, etc.] shall be located in close proximity of the valve plug for testing
purposes => revise Dry Inspector’s Test Connection to comply with these
provisions.